Just before leaving Texas I had a Progressive Industries PT50C Surge/Voltage protector shipped to the stick house. I have 50 Amps at the stick house and tested it out. It worked fine. We left on our trip and I used it in Gulfport, and Pensacola.
When we arrived in Mayport, I again set it up. Came in and shut the generator off and the AC continues to hum. Everything appears normal. So i'm outside continuing the set up and Earlene steps out and tells me whe do not have any plugs working. Her way of saying that the 110V receptacles are dead. So I come in and try the two GFCI resets but to no avail.
Now I start looking at circuit breakers, fuses, and anything else I can find - but no voltage at the outlets. Another look at the PT50C digital readout indicates the code E-0, which means normal operations. Line1 has 119V, Line 2 has 120 V. Line 1 is drawing 0 amps, and line 2 is drawing 21 amps (AC running). So every thing appears normal. I recheck all circuit breakers. Everything is normal, but there is no voltage to the outlets.
So, my dear wife says, "Did you try it without that gadget?" I retorted, "No, there is nothing wrong with that device!!!!"
Well just to satisfy her (and just in case) I went outside, tripped the breaker off, unplugged the PT50C, plug in the umbilical cord to the coach directly into the 50 amp socket, and turned the breaker back on.
The darn receptacles worked. It was a few hours before Earlene siad, "I told you so!" but not exactly in those words.
Anyone, anyone have had this happen and discovered the reason?
I have contacted Progressive Industries. I will have a new PT50C by Friday. I'm anxious to see if it will wrok. Progressive Industries is baffled also and when it is returned they will investigate to see what, if anything, happened.
Welcome to the FMCA Motorhome Forums!
Register now to gain access to all of our features. Once registered and signed in, you will be able to create topics; post replies to existing topics; upload pictures; manage your profile; get your own private messenger; create blogs; and more. Sign up now! Already have an account? Sign in. This message will be removed once you are signed in.
Hmm! PT50C Surge Device
#1
Guest_Wayne77590_*
Posted 30 April 2009 - 09:23 PM
#2
Posted 01 May 2009 - 10:28 AM
2007 Monaco Executive Sandia IV
Cummins ISX 525 Horsepower
Allison 4000 6 Speed Transmission
2006 Saturn Vue
SMI Air Force One
Fort Washington, Maryland
#3
Guest_Wayne77590_*
Posted 01 May 2009 - 04:18 PM
Can't you just hear the conversation:
"Dear, I'll have to shut down all systems, including the air conditioning, but don't worry, I'll have it back up and running by the time you get back. Sorry, I can't go with you. (hee! hee!)
#4
Guest_Wayne77590_*
Posted 02 May 2009 - 08:36 AM
I called Progressive Industries and left a message. The old one will be in the FedEx system today and I asked for a follow up on what was wrong.
Stay tuned!
#5
Posted 11 October 2009 - 01:46 PM
#6
Posted 11 November 2009 - 06:54 PM
2004 KSDP 3706
#7
Guest_Wayne77590_*
Posted 11 November 2009 - 07:35 PM
#8
Posted 12 November 2009 - 01:44 PM
2004 KSDP 3706
#9
Guest_Wayne77590_*
Posted 12 November 2009 - 07:59 PM
And it is backed by the Progressive Industries warranty.
Good luck
#10
Posted 21 February 2010 - 01:33 AM
#11
Posted 21 February 2010 - 06:57 AM
F297108
K4WR
Retired Telecommunications Field Engineer (MCI)
Coach - 2003, H/R Endeavor, 40 Ft
Cummings ISC, 330HP.
Towing 2009, Honda CRV
#12
Posted 21 February 2010 - 03:40 PM
2005 HR Admiral SE 34SBD/W22 Workhorse (optioned out)
2009 Harley ElectraGlide Classic
2006 CR-V toad or
65 GMC G-10 with Harley inside toad or
64 or 62 International Scout 80
2 Years and 11 Months till RETIREMENT!!!!!
#13
Posted 21 February 2010 - 05:59 PM
1st time it said the neutral and ground were reversed when the source was fine, next time it seemed to work OK but had EEEE in the readout, the last time it said the power source was too low, 80 volts, my meter confirmed the source was fine.
Both of the last times the tech argued with me, said the PT50C doesn't ever say EEEE and the last time he said my meter was wrong because they calibrate it before they ship them from the factory.
all 3 times they did repair it under warranty but the last 2 times i had to ship in and be without while they repaired it.
I've read a bunch of great things about Progressive Ind and their products so I'd like to think I just have a bad unit.
#14
Guest_Wayne77590_*
Posted 22 February 2010 - 11:46 AM
Every product can have a "lemon." I'd talk to progressive if you are not happy and see what they can do to replace it. I would hope that they would come to some agreement with you.
Mr. Wilson,
Call progressive and ask them if there are not responses to your question here. I have found them very friendly when i talked to them.
#15
Posted 23 February 2010 - 10:42 PM
The Hughes should be closest to the power pole.
Thomas E. Fanelli, President
Progressive Industries
414B Airport Boulevard
Morrisville, NC 27560
(919) 462-8280
fax: 919-462-6132
tfanelli@progressiveindustries.net
Based on this it appears that an autotransformer will work with this unit. I will let you all know when I get to the Ralley in Albuquerque next month.
#16
Posted 21 March 2013 - 03:40 PM
After considering both the portable and the hard wired surge protector units from Progressive Industries, I'm considering getting the EMS-PT50C portable unit.
I'd like to hear from owners of the portable unit. Any downside to using it? Do you feel it's secure by locking it to the power pedestal?
I'm thinking perhaps of cutting the shore cord inside the bay near the transfer switch, putting male & female plugs the cord, then plugging in the EMS unit in the bay. I could then bypass the unit if it ever failed and had to be sent back for repair.
I appreciate all thoughts and opinions.
#17
Posted 22 March 2013 - 08:47 AM
I have been using the Portable PT50C since 2007 and I use a piece of chain (one that can tow a car) placed around the pedistal and whatever else is near the pedistal, like water spigot. I have never had a problem with it walking off. If someone wants it they would have to use a hacksaw or bolt cutters. It is just something I do. I have been in campgrounds where owners of PT50C's have no provision for securing it. Apparently they have not had any problems either. I prefer to secure my outside expensive items.
As for downsides, other than securing it, I don't have any. I leave it connected to the power cord and just stow it that way. When I pull in it just one thing to plug in and it is ready. I have moved it from a 5th wheel to the Class A and all that was required was to unplug from one and plug into the other. With the permanent model you can take it with you but it is a more difficlut operation.
Consider that some, including myself, have had warranty problems. It is a lot easier to send in the PT50C then the one that needs permanent mounting. Just saying.
Both are great addtions to any RV.